Starting from the sensor, 0.5V to 4.5V will be lowered by the resistor voltage divider by 3300/(3300+1800) or 3300/5100 or 33/51 so
0.5 V * 33/51 = 0.3235 V for 0 psi
4.5 V * 33/51 = 2.9118 V for 2500 psi
Now into the Photon we find
For 0 psi: 0.3235 V / 3.3 V * 4096 steps = 401.56 so the ADC should read about 402.
For 2500 psi: 2.9118 V / 3.3 V * 4096 steps = 3614.11 so ADC level 3614 or so.
So now you can figure that 0-2500 psi maps to 402 to 3614 ADC levels or 0.77833 psi per ADC step. You can read the ADC, subtract 402 and multiply by 0.77833 to get the reading in psi.
In reality, your 3.3V supply will not be exactly 3.3V and there will be noise in the readings.